If you like, skip down for the key question...
BACKGROUND INFO:
What I do NOT have is the circuit breaker, or a decision as to what Amperage said breakers should be at.
THE KEY QUESTION:
* Has Elon (or anyone else) stated (or can anyone deduce) how many 240v single phase Amps or KVA the Cybertruck's on-board Charger can handle?
(FYI: My memory says no.) THAT information will help me to decide exactly how to configure what circuits and conductors go where.
17.088
==========
FYI:
Below is a single phase chart for those of us in the U.S. who do not have three phase, like many in the EU:
First column is the Ampacity of the EVSE device.
Last column is the required Ampacity of the CIRCUIT that the same device should be on.
[{10A x 240v = 2.4kVA (Watts)} x 1.25 = 3000 VA] / 240v = 12.5 Amps
[{20A x 240v = 4.8kVA (Watts)} x 1.25 = 6000 VA] / 240v = 25 Amps
[{30A x 240v = 7.2kVA (Watts)} x 1.25 = 9000 VA] / 240v = 37.5 Amps
[{40A x 240v = 9.6kVA (Watts)} x 1.25 = 12000 VA] / 240v = 50 Amps
[{50A x 240v = 12.0kVA (Watts)} x 1.25 = 15000 VA] / 240v = 62.5 Amps <=====<<
[{60A x 240v = 14.4kVA (Watts)} x 1.25 = 18000 VA] / 240v = 75 Amps
[{70A x 240v = 16.8kVA (Watts} x 1.25 = 21000 VA] / 240v = 87.5 Amps <=====<<
[{80A x 240v = 19.2kVA (Watts)} x 1.25 = 24000 VA] / 240v = 100 Amps
[{90A x 240v = 21.6kVA (Watts)} x 1.25 = 27000 VA] / 240v = 112.5 Amps
[{100A x 240v = 24.0kVA (Watts)} X 1.25 = 30000 VA] / 240v = 125 Amps
=========
==========
My favorite "West Wing" quote (Ep. 1-18): from Sam Seaborn: ==========
BACKGROUND INFO:
In previous years, I have pre-installed:
two 1.5 inch pre-installed PVC conduit(s) going out to the detached garage on the north side of my driveway (length forgotten, but likely more than 100 feet)
and
two (one still available) 1.25 inch PVC conduit(s) going to a post on the south side of my driveway (length forgotten, but likely less than 100 feet).
I also have (100 feet each of) #6 and #4 AWG conductors ready to install for two circuits in one of the conduit(s).(AWG or kcmil) 60°C (140°F) 75°C (167°F)
6 AWG 55 65
4 AWG 70 85
[The 2nd pipe at this location already has a NEMA 14-50 & a 50 Amp circuit installed for the 2nd unit.][CORRECTION:
It looks like I stopped this project after I had purchased a 50 AND 80 amp breaker(s).
I presume the 50 Amp (but probably NOT the 80 Amp.as well) will need to be exchanged for a GFCI version.]
{Note that I _AM_ aware of NEC's TIA 17-2 for Articles 625.44(A), 625.54(New) and 625.56(New)}
Yes, I do know the 2nd version of the Tesla Wall Connector could handle a 100 Amp circuit for 80 useful Amps and the 3rd version can only handle a 60 Amp circuit for 48 useful Amps.
However, I am more interested in finding out...
THE KEY QUESTION:
* Has Elon (or anyone else) stated (or can anyone deduce) how many 240v single phase Amps or KVA the Cybertruck's on-board Charger can handle?
(FYI: My memory says no.) THAT information will help me to decide exactly how to configure what circuits and conductors go where.
17.088
==========
FYI:
Below is a single phase chart for those of us in the U.S. who do not have three phase, like many in the EU:
First column is the Ampacity of the EVSE device.
Last column is the required Ampacity of the CIRCUIT that the same device should be on.
[{10A x 240v = 2.4kVA (Watts)} x 1.25 = 3000 VA] / 240v = 12.5 Amps
[{20A x 240v = 4.8kVA (Watts)} x 1.25 = 6000 VA] / 240v = 25 Amps
[{30A x 240v = 7.2kVA (Watts)} x 1.25 = 9000 VA] / 240v = 37.5 Amps
[{40A x 240v = 9.6kVA (Watts)} x 1.25 = 12000 VA] / 240v = 50 Amps
[{50A x 240v = 12.0kVA (Watts)} x 1.25 = 15000 VA] / 240v = 62.5 Amps <=====<<
[{60A x 240v = 14.4kVA (Watts)} x 1.25 = 18000 VA] / 240v = 75 Amps
[{70A x 240v = 16.8kVA (Watts} x 1.25 = 21000 VA] / 240v = 87.5 Amps <=====<<
[{80A x 240v = 19.2kVA (Watts)} x 1.25 = 24000 VA] / 240v = 100 Amps
[{90A x 240v = 21.6kVA (Watts)} x 1.25 = 27000 VA] / 240v = 112.5 Amps
[{100A x 240v = 24.0kVA (Watts)} X 1.25 = 30000 VA] / 240v = 125 Amps
=========
==========